Stacking issue?
« on: September 30, 2018, 10:21:03 pm »
I recently upgraded my firmware to 2.2, and I now am having issues when I am running two programs at once. I am running a pump out of the canal and have to pressurize the line when I start a new program. One program turns on the valve through the pressure switch and a second program starts a minute later and bypasses the pressure switch for two minutes to pressurize the line. This has always worked well in the past. Since the upgrade, when the two minute program is done, everything shuts down, and I have to put the system on standby and back online to get the line to turn back on. It kind of seems like it is stacking the runs, but I have that option set to "No". I hope this makes sense.

bluespray_admin

  • Global Moderator
  • Sr. Member
  • *****
  • Posts: 327
    • View Profile
Re: Stacking issue?
« Reply #1 on: October 01, 2018, 11:40:06 pm »
It is not stacking.  You probably have the pump connected to the master valve.  When you start a program and specify that you want to run it with master valve on, it'll turn the master valve when the program starts.
Now, if you run a program that starts the pump only for 2 minutes at the same time, it will start the pump, but aster 2 minutes, the pump only program stops and turns off the pump.  I think this is what you're seeing.

If you need to run a program with a pump on for the duration of the program, specify to run the program with master on.  If you need to run the pump for 1 minute ahead of the program, then start the pump only program 1 minute ahead of the other program.