Author Topic: installation of wires to bluespray  (Read 11219 times)

howmanytimes

  • Newbie
  • *
  • Posts: 1
    • View Profile
installation of wires to bluespray
« on: April 08, 2014, 02:53:36 pm »
Trying to install from a hunter system to Bluespary 16 zone controller.

The manual does not help to explain the correct wiring or I just do not under the instructions.

I am hoping someone could help with where which wire goes where to the Bluespray system correctly.

I attached the hunter controller (PC-300i) images of the power side wires.

SEN1, SEN2, AC2 AC1. GND is ground I know that one.  I see a COM black wire (that should match the COM in the bluespray?) and I understand all the zone wires.



BlueSpray 16 zones:
« Last Edit: April 08, 2014, 03:11:17 pm by howmanytimes »

bluespray_admin

  • Global Moderator
  • Sr. Member
  • *****
  • Posts: 327
    • View Profile
Re: installation of wires to bluespray
« Reply #1 on: April 08, 2014, 09:13:23 pm »
Yes, your Hunter's COM goes to BlueSpray's COM, the COM next to M, not the one next to 24V.
If your SEN1 and SEN2 are for rain sensor, connect to RAIN on BlueSpray.
If you have a master valve or pump relay, connect it to M.
If you use our power supply, connect the 2 wires to 24V and CỌM  If you use your hunter's power supply, those 2 yellow wire goes to 24V and COM, I think.  You might want to measure which wires gives you 24V.  We recommend that you use ours.